I've never gone up to 40 KW exactly, but I've configured racks with dual 
PDUs that took 3-phase, 60 AMP service and used IEC 60309 connectors. In 
this arrangement, each PDU can deliver 17.4 KW (might be KVA, actually), 
for just about 35 KW in a single rack.  I used APC PDUs, but I can't 
remember the exact model. It was either the AP8867 or the AP8866. To get 
to 40 KW, you'd need to add a 3rd PDU or go

https://en.wikipedia.org/wiki/IEC_60309#Blue_3P+N+E,_9h

It's my understanding that water-cooled rear door heat exchangers max 
out at about 35 KW of cooling, so you might want to talk to the 
different RDHx  manufacturers to verify their limits before getting too 
far into your design, if you haven't done so already. Coolcentric claims 
their ultra-density doors can handle up to 40 KW.

Everything I've read has said that 35 KW is about the limits for 
air-cooling a rack (Rear door heat exchanger still count as air-cooling, 
since it's air that cooling the computer components), and beyond that 
you should start looking at direct contact liquid cooling, like products 
from Asetek or CoolIT systems.

That's my 2 cents.

Prentice

On 10/21/19 11:50 AM, Michael Di Domenico wrote:
> Has anyone on the list built 40kw racks?  I'm particularly interested
> in what parts you used, rack, pdu, rear door hx, etc.
> _______________________________________________
> Beowulf mailing list, Beowulf at beowulf.org sponsored by Penguin Computing
> To change your subscription (digest mode or unsubscribe) visit https://beowulf.org/cgi-bin/mailman/listinfo/beowulf


More information about the Beowulf mailing list