I did a similar project last fall. The only unpleasant surprise is
that most UPS are capable of running continuously at 80% of their kVA
value. So you may want a larger system.
You can get more current when you go to a three phase UPS system.
On Wed, Apr 29, 2009 at 7:46 AM, <vlad at geociencias.unam.mx> wrote:
> Hi,
>
> I have a linux cluster and need to purchase a UPS system.
> The total expected current consumption will be 240 amps. At 120 V this
> would require a 30 kVA UPS system.
> However, I see that 30 kVA systems have a limitation for the input
> current. For example, this 30 kVA system
> (http://www.provantage.com/tripp-lite-su30k3-3xr5~7TRPL1Q9.htm) allows
> only 90 amps as input
> current. I am a bit confused here, and I need some advice on what UPS
> system I should look for.
>
> Thanks,
> Vlad
>
> _______________________________________________
> Beowulf mailing list, Beowulf at beowulf.org sponsored by Penguin Computing
> To change your subscription (digest mode or unsubscribe) visit http://www.beowulf.org/mailman/listinfo/beowulf
>
--
-----------------------
Thanks
Tom