Robert G. Brown wrote:
> As I'm working up a server room and some UPS's, a question arises. The
> APC units we have have a different plug and current rating from the
> circuits in the wall. In particular, we have L6-30R receptacles and the
> APC requires only 20A. I had thought that it would be perfectly safe to
> replace an L5-20P with an L6-30P and plug a 2200 VA UPS into a 30 amp
> circuit, but the electrician who was doing some of the rewiring said "we
> can't do that" because "the 30A circuit breaker might not blow in time
> to protect" the 2200 VA device from damage in the event of an internal
> short.
>
> This argument seems quite senseless to me. If this argument were
> correct we could never plug a 15 A device into a 20 A circuit, etc. It
> would really simplify my life if I can just rehead the cable. Do any of
> the electricity-savvy people here have any comments regarding the safety
> or legality of doing so? I have always assumed that going up a size in
> circuit capacity is generally safe and legal...
>
> I'm planning to do the rewiring of cables today soon, so if you know
> something about his please respond "soon".
>
> rgb
>
The code says that a single receptacle on a circuit must have a rating
at least
as high as the circuit breaker, so you can't change the receptacles to
L5-20R's
unless you change the breakers too.
Here's an adapter that does what you want.
http://www.stayonline.com/detail.aspx?ID=3105
Counting labor, it might be cheaper than rewiring the cords.
-L