Electrical codes and plugs/sockets was Re: [Beowulf] Opteron cooling specifications?
Bruce Allen
ballen at gravity.phys.uwm.edu
Mon May 1 12:00:41 PDT 2006
In our experience it's a very good idea to observe the "don't operate a
circuit at more than 80% of rated capacity". We just had to replace a
150A 3-phase breaker which died after being operated a bit too close
(within 10A) of its rated capacity for a number of months.
Cheers,
Bruce
On Mon, 1 May 2006, Jim Lux wrote:
> At 08:41 AM 5/1/2006, Mark Hahn wrote:
>> >
>>
>> > We've being switching cabinets in one of our datacenters to 220volt
>> > service to support the sort of density we're seeing without running new
>> > conductors.
>>
>> sure, there's no downside to 220 afaikt. one thing I don't fully
>> understand is where the 80% figure comes from. just a fudge-factor,
>> and what if you wind up always using that extra capacity?
>> presumably an L6-30 circuit is actually safe to run at 30...
>
>
> The electrical code usually requires that a circuit be wired (and overcurrent
> protected) so that the expected load is no more than 80% of the circuit
> ampacity. If you don't have a specific design, then the expected load is
> calculated by using a set of rules that turn square feet of floor space and
> what that space is used for (offices are different than residential are
> different than a parking lot). There's also rules for certain specific kinds
> of loads and locations (i.e. you have to have 20 Amp circuits for a
> refrigerator in a kitchen) and rules about what kinds of loads can be shared
> (no combining the lights and the receptacles in a kitchen).
>
> "L6-30" is a NEMA designation for a particular form of pins in the
> plug/receptacle. "L" for locking. 6 for the particular configuration of pins,
> and it's nominal usage: The 30 refers to convention for what that
> plug/receptacle configuration is used for (i.e. a 30 Amp circuit, intended
> for use at 24 Amps)
>
> Bear in mind, also, that the various configurations will have designs
> compatible with the nominal use. For instance, a configuration designed for
> 30A service will accomodate AWG10 or AWG8 wires, typically larger on the
> receptacle (female) than on the plug (male). There's also voltage ratings
> that apply to each configuration. That is, a connector designed for 480V
> service will be rated for 600V, and have different clearances internally than
> a connector designed for 120V service, rated for 300V.
>
> It is not unheard of to have NEMA plugs and receptacles used on circuits with
> ratings different than the nominal. For example, some of the other 4 wire
> connectors for 277 or 480V are used on 230V circuits, just to provide
> different, non-inadvertently-interchangeable pin configurations. For
> instance, you might have a motor controller that is supplied with a L15-30
> (30A, 3ph, 250V rating) from the wall, and the motor is connected using a
> L17-30 (which is normally on a 480V 3ph line). This is why you should always
> check before blindly plugging something in.
>
> James Lux, P.E.
> Spacecraft Radio Frequency Subsystems Group
> Flight Communications Systems Section
> Jet Propulsion Laboratory, Mail Stop 161-213
> 4800 Oak Grove Drive
> Pasadena CA 91109
> tel: (818)354-2075
> fax: (818)393-6875
>
>
> _______________________________________________
> Beowulf mailing list, Beowulf at beowulf.org
> To change your subscription (digest mode or unsubscribe) visit
> http://www.beowulf.org/mailman/listinfo/beowulf
>
More information about the Beowulf
mailing list