[Beowulf] powering up 18 motherboards
Alpay Kasal
eno at dorsai.org
Thu Feb 17 23:25:22 PST 2005
I think you hit the nail on the head Bari, I'm in Brooklyn, New York. So I
suppose it should be 15amp circuits but every circuit breaker in the box is
clearly a 10. This is an old house, seems like any renovations over the
years have been only for aesthetics. The wiring in the walls is probably
disintegrating - that would explain why the new looking circuit breakers are
rated for 10 amps.
I think I can get use of 3 circuits which gives me some room to play with
all the nodes and hopefully the assortment of switches and power supply. I
have to figure out what the draw will be on the rest of the equip. Now where
the hell am I going to plug in this air conditioner????
Any advice on how to gang up 3 10amp circuits into a single 30amp? Sounds
like a job for an electrician? Thanks for the help guys.
Alpay
-----Original Message-----
From: Bari Ari [mailto:bari at onelabs.com]
Sent: Thursday, February 17, 2005 8:00 PM
To: Jim Lux
Cc: Dean Johnson; Alpay Kasal; beowulf at beowulf.org
Subject: Re: [SPAM] [Beowulf] powering up 18 motherboards
Jim Lux wrote:
> A 10 amp circuit would be highly unusual in the U.S., but might be
> common practice elsewhere. In the U.S., a 15 amp circuit is standard.
I thought this was odd when I first read this as well. This may be a
case where to save dollars or in rehabbing old buildings where you may
have more than 3 current carrying conductors in one raceway and you have
to derate the current protection. In this case it may be that they ran
more than three #14 current carrying conductors (as defined by the
NEC)in the same raceway and had to derate the usual 15 amp circuit
protection down to 10 amps.
-Bari Ari
More information about the Beowulf
mailing list