egads, IBM has terminal constipation of the documentation. it's impossible
to find anythign about the dissipation of a blade. I'm guessing it's
about 150-200W per dual. 168p/rack. 13-17 KW/rack.
it's interesting to contrast HP's blades. we looked at their bl35p
(dual-opteron) - it has admirable density (192p/rack), and opterons
are both reasonably fast and reasonably cool. but if you actually
follow the blade mentality (density matters), you quickly wind up with
racks dissipating 20+ KW (and that's not even counting the possibility
of dual-core, dual-socket blades!) depopulating racks to make them
easier to cool seems rather silly.
consider that for 20KW, you basically need 7 tiles per rack to
provide cold airflow. you might be able to get that down to 3 or so
with high-perf tiles, over-rack coolers, etc.
AFAIKT, with current dissipations, blades are only viable for machinerooms
which need a late-life kicker - say, put a single rack of blades in a room
filled with low-density stuff (and crank up the airflow some). rows of
fully-populated blade racks seem to be a real dissipation issue.
remember that a 1U dual-socket, dual-core server is 4p/u - the same density
as marenostrum. of course, it may not be desirable to divide interconnect
among 4p...
now, if we could only get vendors to agree on a standard, flexible heatpipe
connection scheme ;)