On Mon, Oct 21, 2002 at 11:28:09AM -0400, Robert G. Brown's all...
> Most standard circuits have enough capacity to run two duals or four
> singles - you can estimate that they'll draw somewhere in the vicinity
> of 400-600 Watts, which is roughly a third the capacity of a twenty amp
> circuit for a switching power supply load, more like half the capacity
> of a 15 amp circuit. Then you've got a monitor and network switch,
> which can be another 100-200 Watts. A beefy UPS is not a bad thing to
wow. thats huge. I had 8 dual 2466s with 1.3tbirds on a 15Amp circuit (no
disk). When I moved it to a new building, I am guessing that the voltage was a
bit different, and the power bars they were wired into started blowing.
(perhaps they were drawing more amps at a lower voltage than my install
area?) At any rate, I put them in 8 per 20 amp circuit (instead of my
original intall 8/15) and nothing has blown (oh, and only 4 per power bar
too now :). Are you spec'ing for some seriously heavy disk power loads?
[A friend told me about blowing a circuit once at his lab and he had a large
metal bracelet on. When the circuit blew, he was standing under the power
run (about 5 feet over his head in the ceiling) and his bracelet shot up his
arm and yanked on his wrist, quite hard! He had a bruise to prove it. It
was only a 20A circuit - what would cause that? Dangerous wiring situation?]
> For that reason you might well want to select systems based on their low
> power requirements rather than their speed...
Has anyone here actually done this based on a full TCO analysis where
operations cost were as large (or larger) a factor than initial install?
Are TMTA's worth it in this situ?
/kc
>
> rgb
>
> >
> > ---------------------------------
> > Do you Yahoo!?
> > Y! Web Hosting - Let the expert host your web site
>
> Robert G. Brown http://www.phy.duke.edu/~rgb/
> Duke University Dept. of Physics, Box 90305
> Durham, N.C. 27708-0305
> Phone: 1-919-660-2567 Fax: 919-660-2525 email:rgb at phy.duke.edu
>
>
>
> _______________________________________________
> Beowulf mailing list, Beowulf at beowulf.org
> To change your subscription (digest mode or unsubscribe) visit http://www.beowulf.org/mailman/listinfo/beowulf
--
Ken Chase, math at velocet.ca * Velocet Communications Inc. * Toronto, CANADA
More information about the Beowulf
mailing list